Dear community,
Dear Victron,
I am looking at installing an EasySolar 24/3000 in an RV. I am scratching my head about the wireing diagram in Appendix B. Is this correct? Doesn't look safe... (see red circle)
I see multiple safety issues:
1. If N and L are swapped in ACin, L is directly connected to PE
--> When connecting shore power in a non-stationary setup, it is not guaranteed what L and N is. As long as CEE is used, this is standardized. Most other power connector do not have this guaranteed
2. built-in RCD is not useful in this case.
--> reliance on a correctly installed RCD in the shore power installation
3. Even though there is a RCD in the shore power installation, there will be a small delay for the RCD to kill the lines when plugging in
--> unsafe for a couple of ms, unneccary
4. EVEN IF everything is according to the diagram, N is connected to PE!
--> not allowed in any country I know when a PEN was divided into PE and N earlier in the installation.
So: Is this diagram correct or not? Could it be that PE from shore power / ACin is connected to the ground relais instead of N? That would be the end of the story and all would be fine, I think.
Thx for the help!