DC ripple with quattro and BYD

hello guys

we are facing a weird situation in one of our system since we made the installation till now.

the system is composed of ( 16 kwh LVS BYD + 15 kva quattro + 32 X 400 wp trina solar panel connect to 3 250/100 mppt as 12 pvs /1 mppt)

since the first day we are phasing a dc ripple issue it always happen in the after noon between 11 am to 1 pm the system

we have installed many systems like this combination and they are working perfectly

the byd and the ve configure is same as the Victron and BYD recommendation the type of the cable used are 70 mm and the length is less then 1.2 meter whatsapp-image-2022-07-20-at-105736-am.jpegwhatsapp-image-2022-07-20-at-110032-am.jpeg

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@eyub

15kVa Quattro uses 2x 95mm² cable for negative and 2x 95mm² for positive. I would start with changing that.

See the quattro printed manual on page 9.

The DC ripple can either be heat (high resistance connections) or the battery voltage or some cell voltages going too high. The only way to determine which is to see more data.