Hi, I need to install 3phase system without neutral 220VAC, is possible to make this configuration with 3 multiplus?

I understand to make this configuration with 3 multilplus 120VAC, but What do I do with the neutral?


MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

It is not possible to make a Delta configuration. Only Wye. It is because without a neutral, the inverter has no reference point with which to regulate its output Voltage.

The only way I can think of is to use a Wye / Delta transformer after the inverters.