Node red, ideas to force AC2 out on with grid failure

Fairly sure the answer is no, I am trying to find a way to force AC2 out on during grid failure via node red dashboard.

The current nodes don't seem to have this ability and the assistant in the multi is cumbersome.

Would be cool to be able to control that relay via node red.


Multiplus-IINode-RED
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
biff-trotters avatar image
biff-trotters answered ·

In Assistants, choose programmable relay. Use ACOUT 2 relay. Set to On. Conditions AC input. Drive relay for AC input not available.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

biff-trotters avatar image
biff-trotters answered ·

...and likewise, you can drive it OFF for grid available.