Good morning everyone
i would like to know if i can work with 3 isolation transformers in parallel because i need 21KW
thanks you
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Good morning everyone
i would like to know if i can work with 3 isolation transformers in parallel because i need 21KW
thanks you
I would not like to attempt this. In theory it would work, but you are very likely to run into issues with balancing the load evenly across all units. They are passive devices.
Manufacturing tolerances and mismatches in cable length play a critical role in current sharing between such devices.
Passive isolation transformers are unlike paralleled active devices like Quattro's which can chat amongst one another to actively balance the load between themselves. Additionally, active devices are calibrated to bring the tolerances between them much closer.