Smartsolar MPPT 100/30 shows maximum 30 amps. At the same time the Smartshunt 500/50 shows 28,5 amps. Is it a way to have the shunt adjusted to show the correct amps ? It is a standalone installation.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Smartsolar MPPT 100/30 shows maximum 30 amps. At the same time the Smartshunt 500/50 shows 28,5 amps. Is it a way to have the shunt adjusted to show the correct amps ? It is a standalone installation.
You mentioned a clampmeter? Post a photo regarding readings.
picture showing that MPPT and clamp meter shows approx 30 and shunt 28,5
I think that the SBS bat neg lug should be relocated. Re surface area.
The MPPT reading (30A) and the clampmeter reading (29.7A) are pretty close. I an assuming the clampmeter is on a MPPT battery wire.
The current exiting the MPPT charger might go to power some loads, not necesarilly to charge the battery. So some or all of it might not pass through the shunt. That's actually the main reason to buy a SmartShunt/BMV.
@klim8skeptic I think you are right about the neg lug of the SBS. I relocated it now immediately. It did not change anything. ( I guess the load of the SBS is negligible )
@Seb71 The only load in the system is an inverter. During these tests the cable to it is disconnected. So there is no load connected.
Being frustrated that the shunt show to little amps, I have now fixed it. I really think it is bad that the accuracy was so bad.
How I fixed it. I used a file on the shunt to little by little take away metall until it shows the correct current. You should not have to do it this way but now all reading are the same.