question

nimrod avatar image
nimrod asked

Sunny boy sb 3000 manufacture 2012 ac coupling

I would like to buy a old but Nevers used sma sunny boy SB 3000 inverter manufactured in 2012 for making ac coupling. But how to know if thé fréquence shift work with this old modele?

Thanks

ac coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
sharpener avatar image
sharpener answered ·

Yes I think the Sunny Boy will have to include frequency shift in the spec because they were designed for the German market and in 2012 the German grid code required it.

I have Steca inverters (also German) manufactured in 2011 and it is part of their spec too. Upper limit for normal operation is 53 Hz and I have the 3 frequency settings in VE Configure set to 53.1, 53.2 and 53.3 Hz (they have to be different). In loss-of-grid/island mode the shutdown on over-frequency works correctly to prevent excess PV generation.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nimrod avatar image
nimrod answered ·

Thank you.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sharpener avatar image
sharpener answered ·

My mistake, the settings in my ESS Assistant are 51.1, 51.2, 51.3 Hz, not as originally stated above.

You do not say what country you are in, here is the table for my StecaGrid 2000s which may help in setting up the Victron eqpt to work with your Sunny Boy:

1657482838803.png



1657482838803.png (101.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.