Overload 24/3000 Phoenix

Hello my friends,


I have a problem with a Phoenix 24/3000 Inverter.


When i switch ON the inverter it is immediately overload. Even with No load.


I measured the continuity between Phase and Neutro, and i have a value close to 0 ohm.


I measured the output of two transformers and both have a value of 1,8 ohm.


Do you have a idea of a problem?

Phoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Elimac avatar image
Elimac answered ·

Is this a new installation? If so, it could be the problem of charging the internal capacitors. You may need another source to help the initial startup. The inrush current may be too high.

What do you mean "continuidade entre Fase e neutro close to zero"? You should check only the loads, guaranteeing there is no short circuit, but disconnect from Inverter while measuring, or you are actually measuring its output impedance... kind of...