Just curious because from the positive output terminal of the 150/35 charge controller, I'm getting 300-600 ohms, and on the negative terminal I get 0 ohms. Should it be 0?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Just curious because from the positive output terminal of the 150/35 charge controller, I'm getting 300-600 ohms, and on the negative terminal I get 0 ohms. Should it be 0?
strange question. What are you trying to measure? if you measure the resistance from one negative terminal of an mppt to the other ( bat to PV) it will be zero, as these are internally connected together.
The PV + to bat + involves all of the internal electronics, so these are not connected together, and measuring the resistance between them is not an indication of the functionality of the unit.