friaras avatar image
friaras asked

What is the resistance value on the 150/35 charge controller's output pos and neg terminals?

Just curious because from the positive output terminal of the 150/35 charge controller, I'm getting 300-600 ohms, and on the negative terminal I get 0 ohms. Should it be 0?

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

strange question. What are you trying to measure? if you measure the resistance from one negative terminal of an mppt to the other ( bat to PV) it will be zero, as these are internally connected together.

The PV + to bat + involves all of the internal electronics, so these are not connected together, and measuring the resistance between them is not an indication of the functionality of the unit.