question

jwareham avatar image
jwareham asked

Solar charge controller question

Hi all,


I am hoping to wire up a 180 watt solar panel to my Victron MPPT 75/10 solar charger. I understand that this should be wired into the distribution blocks. I was wondering what amp midi fuse I should use for the positive distribution block, I am using 4mm squared cable. The guide I have purchased states 10 amp, but they don't seem to exist!


Thanks in advance,


James

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
dansonamission avatar image
dansonamission answered ·

Not sure what guide you are looking at by the manual on page 10 indicates between 15A and 20A fuse for the 75/10

https://www.victronenergy.com/upload/documents/Manual_SmartSolar_MPPT_75-10_up_to_100-20/MPPT_solar_charger_manual-en.pdf

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image
klim8skeptic answered ·

Unfortunately you can not find a 10a midi fuse.

You could use 6mm cable and a 30a midi fuse to protect the cable between the battery and mppt.

30a midi fuse.

test.


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cairnsbakeryinfo avatar image cairnsbakeryinfo commented ·
test.
0 Likes 0 ·