question

padmika avatar image
padmika asked

Portal Not Showing AC Input for Multiplus

1654737620005.png

Hi,

I have a multiplus charging batteries and load also from output of Multiplus. The system is working fine, but the portal complains AC Input Not Available. Don't see any alarms when i log into cerbo. Software is up to date.

Any idea why it doesn't see AC Input?

Thanks,

Padmika

Multiplus-IIVRM
1654737620005.png (152.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Did you configure the AC input in the settings of the Cerbo?

Settings -> System-Setup -> AC-input 1

The default setting is "not available" and it has to be changed to something else.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

s1277 avatar image s1277 commented ·
always forget this after storage
0 Likes 0 ·
padmika avatar image
padmika answered ·

Now showing.

Thanks for your help.

2 |3000