Falsches anzeigen bei AC Last

Hallo Leute

könnte mir bitte jemand sagen was ich einstellen muß, das mein Wechselrichter, der Direkt auf L1 1 Phasig einspeist, NICHT in der Remote Konsole als AC LAst angezeigt wird??

Es soll nur der momentane Ertrag angezeigt werden.

Habe alles versucht, leider ohne Erfolg. S. Foto


Gruß Martin

022390cd-3166-4871-923e-24c7b5846c30.jpeg

52ab7bd6-8a90-4439-ba21-af227d501c54.jpeg

Multiplus-IIESSVenus OS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

19 Answers
maha avatar image
maha answered ·

Welche Rolle hast du für den Zähler eingestellt? Unter "Energiemessgeräte"...

Sollte dann PV-Wechselrichter und nicht Netzzähler sein:

1654257722372.png


1654257722372.png (21.3 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

martinka avatar image martinka commented ·
das hatte ich falsch, danke jetzt läuft es
0 Likes 0 ·
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Bin mir nicht sicher, ob ich das richtig verstanden habe, aber wenn der PV-Wechselrichter vor dem Victron System ins Netz einspeist, muss oben auch AC Eingang ausgewählt werden.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

martinka avatar image
martinka answered ·

Also ich habe das System so aufgestellt, das ich eine usv habe, das heißt die MP Sind vor dem nezt. Der alte WR speist auf L1 ein. Und in der Remote Konsole erscheint der Ertrag vom WR als aC Last. Man kann doch den Ertrag irgendwie ausblenden oder?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

martinka avatar image
martinka answered ·

Hallo noch mal,

leider hat das richtige Anzeigen WR-Ertrags nicht funktioniert.


Es ist immer noch so, das der aktuelle Ertrag in der AC Last einbezogen wird. Ich habe es getestet, in dem ich den WR vom Netzt nahm und die AC Last auf L1 runterging. WR wieder an und direkt die Last auf L1 um den wert des WR Ertrag nach oben ging.


Wenn ich den WR in den Einstellungen auf Anzeigen nein setzte dann passt es, Nachteil ist das ich in der Remote Konsole nicht sehe was der WR gerade produziert.


Hat jemand noch eine Idee, was ich noch machen kann, das die AC Last richtig angezeigt wird(ohne den Ertrag vom WR) und trotzdem in der Remote Konsole der Ertrag ersichtlich ist??

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

Kannst du mal eine Skizze machen, wie die Anlage verkabelt ist?
Bitte auch mal eine Auflistung aller verbauten Komponenten.

0 Likes 0 ·
martinka avatar image
martinka answered ·

Bin kein Fachmann und hoffe du kommst klar damit.piktogramm-anlage.jpg


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

martinka avatar image
martinka answered ·
Hallo habe die Skizze erstellt.
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Glen avatar image
Glen answered ·

1663858271105.pngHallo,

ich klinke mich mal in diese Diskussion ein da ich genau das selbe Problem habe.

ich habe nun testweise meine beiden "Microinverter/Balkonkraftwerke" Anlagen mit jeweils EM24 und als PV Inverter im Cerbo programiert . Eins mal im AC-IN und eins im AC-Out1


Anlage ist Insel(seriell) 3 Phasen ESS 48/5000er mit einem MPPT450/100

Aufbau = SLS , Stadtwerke Zähler , EM24 , Umschalter Netz/0/Victrons

das gesamt Haus hängt bis auf 2 Sachen im AC-OUT1 der 3 Victrons (eigene N-Leitungen)




ich bekomme es ums verrecken nicht hin das er die PV-Inverters SUBTRAHIERT und nicht addiert .

so läuft alles perfekt, aber diese "kosmetische" Anzeige ist verwirrend ....

Dsa komische dbaei ist auch das er Phase 1 quasi einspeisst und beim Out bei Phase 3 auf 0 regelt in der Anzeige . Bei Anzeige "Netz" oben links ist die Phase3 dann im Minus ( ok er saldiert ja runter )

Bei AC-Lasten auf Phase1 zeigt er mir den "AC-IN" PV Inverter als positive Last und in den kritischen Lasten addiert er mir den "AC-Out1" PV Inverter auch einfach hinzu ...

komisch .....



Gruss Glen

Anbei meine Anlage :


solar.gcpool.eu




1663858271105.png (246.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Glen avatar image
Glen answered ·

hier mal den MPPT ausgeschaltet :


1663858366217.png



1663858476184.png

und nun in den Abendstunden wenn die beiden Microinverter/BalkonAnlgaen aus sind :

1663866637843.png

jetzt stimmen die Anzeigen wieder



1663858366217.png (635.8 KiB)
1663858476184.png (48.0 KiB)
1663866637843.png (243.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

thomas007 avatar image
thomas007 answered ·

Hallo zusammen,

Ich habe genau die gleiche Problematik das mir den "AC-IN" PV Inverter als positive Last bei den AC Loads anzeigt.

Hat hier jemand vl. inzwischen eine Erklärung bzw. Lösung für dieses Phänomen?

Wäre da sehr dankbar darüber.


Danke.


MFG

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sven23 avatar image
sven23 answered ·

Hallo zusammen,

Ich habe genau das gleiche Problem. Meine OpenDTU Inverter (eingebunden über den script von (henne49)) werden als positive Last bei den AC Loads anzeigt.


In der config als "AC-IN" PV Inverter werden die OpenDTU Inverter garnicht angezeigt.

In der config als "AC-OUT" PV Inverter werden sie angezeigt, jedoch werden die AC Loads falsch gezählt.

Mir ist zudem aufgefallen, dass nur bei negativen grid-meter Leistungen (also Einspeisung je Phase) die AC Load Berechnung falsch ist.

Bei gerunger PV Leisung und zusätzlichem Bezug (grid-meter Leisung positiv) stimmt die AC Load Berechnung.


Gibt es hierfür schon eine Lösung?


Danke und Gruß

Sven


PS: venusOS Firmware: v3.10-32

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

schnail avatar image
schnail answered ·

Gibt es zu dem Thema Neuigkeiten? Ich stehe vor dem selbigen Dilemma und Frage mich was hier der richtige Weg ist?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ar-wi avatar image
ar-wi answered ·

Schließe mich @Schnail an. Habe das gleiche Problem. Updates dazu?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Glen avatar image
Glen answered ·

@Matthias Lange - DE

@mvader (Victron Energy)


Please can you help? its an Problem which isnt fixed since 1 Year

as shown below there are microinverters connected to 2 EM24 on the LEFT side ( 2 different PV )


the original Fronius and the MPPT works well and calculated correctly

but the 2 microInverter/BKW calculated from EM24 (both) are ADDING to AC-LOAD! and overall it ADD! the complete Power and not SUBTRACT ...


it is the same if i put it on AC OUT oder AC IN. on AC OUT it will be add the same Amount and not subtract.

Both of the EM24 are plugged on L1 an the Wiring on Top of the EM24 goes to PV ( as shown on FaQ ) if i turn the Cabels it shows negative Values


Please take a look if you have Time

(Sorry English isnt my native Language )


Edit : its an 3Phase ESS serial! System

for a closer look you can go to : http://solar.gcpool.eu

Edit2:

a shown below you see "PV-Wechselrichter" on the LEFT (1437W) are the 2 Em24PV"Inverter"

it adds on L1 at AC LOAD and adding this Amount to TOTAL "Ac Load+Critical Load" (3638W)

but must be only 2125W Critical , hope you can understood what i mean

if i put the 2 EM24"Inverters" to AC OUT it ADD the Amount to Critical Loads, its no different if i put it on ACIN or ACOUT its always adding the Power



The Enclosure works like Charm since Mid2023 but the Calculations are wrong in VRM.


1705747747256.png

works like Charm since
1705747382091.png


1705747320164.png


1705746015472.png


1705745992967.png1705745967338.png1705745833656.png


1705745833656.png (169.8 KiB)
1705745967338.png (60.0 KiB)
1705745992967.png (63.7 KiB)
1705746015472.png (42.6 KiB)
1705747320164.png (59.6 KiB)
1705747382091.png (19.9 KiB)
1705747747256.png (191.3 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·
Schaltplan?

Auf welchen Phasen sind die Wechselrichter?
Stelle die EM24 mal auf 3-phasig um, auch wenn die Wechselrichter nur 1-phasig sind.

0 Likes 0 ·
Glen avatar image
Glen answered ·

Moins ,

Schaltplan gerade nicht zur Hand . ist aber ein 3phasiges serielles Konzept.

Kommend vom Zähler auf einen Hager406 (Bypass) direkt zu den Victrons und dann erst komplett wieder ins Haus "QuasiInsel" . das gesamte Haus hängt somit hinter den Victrons (AC OUT) als serielles System.


Normalerweise müsste ich ja auch die Micros auf Stellung ACOUT legen was aber zur Folge hat das er die Werte auf die Kritischen Lasten ADDIERT , daher habe ich sich auf Stellung AC IN gesetzt damit das zumindestens klarer in der Berechung ist was das Haus verbraucht

zur PhasenFrage : beide real gemessen auf L1, habe auch schon mal einen komplett rausgenommen zum Testen verringert sich halt nur die PV/AC Last

beide auch auf unterschiedlichen LS und Verkabelungen, kreutzen oder kommen sich garnicht selbst ins Gehege


Ich habe nun beide MicroAnlagen auf 3P.n mal geschaltet ( ich meine mal das ich das auch schon probiert hatte )

Mal gucken was nachher passiert

Denn eigentlich läuft die Anlage mehr als perfekt und hatte keinerlei Bauchschmerzen bis jetzt ausser diese Berechnung die nicht passte .

Kann man AC-Lasten evtl einfach nur "ausblenden" ?


Gruss Glen


1705823424679.png




1705823424679.png (43.5 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·
Wenn die PV Wechelrichter physikalisch am AC OUT sind, musst du das auch auf AC OUT einstellen.
0 Likes 0 ·
Glen avatar image
Glen answered ·

habe ich sobene gerade nochmals gemacht, die Sonne muss erst noch mal hochkommen. Denke aber mal er ADDIERT wieder auf Kritische Lasten.

also ich habe umgestellt auf 3p.n und auf ACOUT


wenns nicht klappt, was waäre dann noch möglich ?


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Glen avatar image
Glen answered ·

die beiden EM24 (micros) belasse ich auf 3p.n . das einzigste was man noch probieren könnte wäre auf 1P umzustellen, richtig ?


1705825537588.png


1705825537588.png (40.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Glen avatar image
Glen answered ·

also die "logische" Anzeige passt zumindest jetzt bei wenig PV :

L1 bei PV WR hat er die Micros addiert ( Symo 3Phasiger + L1 "ontop" )

jetzt muss man nur beobachten ober er die zusätzliche L1 Leitung noch bei Kritische Lasten evtl wieder draufpackt ( was ja falsch wäre )

wird sich zeigen wenn die Sonne brennt


1705827000266.png



1705827000266.png (166.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Glen avatar image
Glen answered ·

nope, er ADDIERT es auf L1 bei den Kritischen Lasten . Passt leider so nicht.

das einzigste was mir noch einfallen würde wäre =


Aktueller Stand =

OBEN am EM24 die PV Seite angeschlossen und UNTEN L1 sowie N weiter zum HAK

Versuch=

drehen der L1 oben unten(negativ Anzeige )


würde das was bringen ?

wie gesagt die Anzeige nun rein bei dem "PV-Wechselrichter" ( Symo und die beiden Micros ) passen ja = L1 ist nun mehr W drauf

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Glen avatar image
Glen answered ·

Gelöst !! , Danke an @Matthias Lange - DE


Jetziger Zustand :


1706342234213.png


was wurde gemacht :


beide Em24 die als PV Inverter mitlaufen auf 3p.n gestellt und was ganz wichtig ist = WARTEN ! es dauerte ein paar MInuten bis das richtig angezeigt wird/wurde (Berechnung)


1706342373434.png


weiterhin habe ich die beiden Em24 mal hin un her geschaltet von AC IN auf AC Out . VRm zeigte es zwar sofort an aber addierte das ganze immer noch , daher auch hier warten ... warum, weiss ich nicht ...

zumindest klappt es jetzt bei mir und es wird die Last ( hier L1 zusätzlich beim PV Interver ) nun RICHTIG berechnet .


Danke für die Mithilfe