GERBO GX digital inputs for burglar/door alarm.

Good day

I would like to use the digital inputs for a burglar/door alarm. I would like to use a vibration sensor for the alarm contact. The relay on this sensor is not latching. It is a pulse relay that resets automatically after about one second.

Will this work to see a alarm trigger on the VRM portal? Or must the sensor used as the alarm contact be latching?

cerbo gx
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Yes, the alarm contact should be latching to maintain an alarm state.
The inputs are not latching and the alarm state will clear as soon as the contact returns to a normal position.