I have the victron battery protect 12/24|65 with my battery AGM Super Cycle of 170 Amp?
Thanks!
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello!
I have the victron battery protect 12/24|65 with my battery AGM Super Cycle of 170 Amp?
Thanks!
What are you trying to achieve with the SBP, switching the inverter off in case of low battery?
Lo siento, la foto del inversor fue un error. La duda es que numero de programa o configuracion necesito con la bateria protect 12/24|65 con mi bateria agm super ciclo 170Am. Gracias
Depending on type of loads I think 10.5V / 12V = A0 or b0 (depending on buzzer/LED or relay mode) seems to be a good compromise. This allows also for heavy loads with a huge voltage drop.
If you are running light loads, then raise the disconnect level to ie. 11.5V / 12.8V = A6 or b6 (depending on buzzer/LED or relay mode).
I will use led lights, frigo (45,watts/hour used) pompe l'eau, and a the conversor of the photo (maxim 1 hour for day) using DMC control in mode 3.