Hi,
I have a grid-connected system (no feedback) with Multiplus 3000/24/70 and VenusGX.
I can run most of my electronics from the inverter, but when it comes to the washing machines (2000W) the inverter can't cope since there is additionally some 200W to 400W AC loads connected. So, I have set a condition to switch to grid if AC loads > 1800W. But to take advantage of Solar, I have put a limit in the AC input in the order of 3 to 6A. This will make the System use Powerassist and use much of the Solar (either direct or from battery) and get another part of energy from Grid.
The issue that I want to address is that if I want to really take advantage of solar - I have >3000Wp installed, I would like the inverter to fetch from grid only what it really needs to complete the AC loads needs. That is, use the Maximum AC load that I set as condition to switch to grid to be the inverter set point (in my case 1800W) and get the remaining from grid.
Instead, what currently happens is that system will use the maximum that it can from Grid and then complements with Solar. I would like this in reverse...
Is there any way to do it?
(note: I can't use ESS...)