Inverter Parallel Compatibility

Hi Guys,

With different version of the Victron Multiplus 1/2 out now, Is there a compatibility chat-table of what can work together ?

I understand previously both devices must be identical ? is this still the case?


Regards

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

@Denzel

nothing has changed. All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set.

See also the Parallel, split- and three phase VE.Bus systems guide.