Temperature sensor for BMV-712 Smart and BMV-702 with Battery Terminal Fuse?

I have a terminal fuse attached to the POS terminal.


Should the temperature sensor be connected to the battery or the fuse?


I would prefer the fuse, but would that get in the way of a good battery reading?

BMV Battery Monitorterminals
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·

Sensor should be on the battery. Not sure why you think it's going to affect the battery reading.

0 Likes 0 ·
platypus avatar image platypus kevgermany ♦♦ commented ·
I don't think connecting it to the battery would affect the reading. My concern was that by connecting it to the terminal fuse instead of the battery might make the temperature reading less accurate, but i'd prefer to put all loads after the terminal fuse for saftey.
0 Likes 0 ·
1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

For an accurate temperature (and voltage) reading the sensor should be connected directly to the battery.