Hey there,
I'm planing an ESS system for the site of an NGO in Peru with following specifications:
- Unstable 3-phase grid (star type, 60Hz)
- 3x Quattro-II in 3-phase config (5kVA, 48V)
- 3-phase Genset (~15kW prime, 60Hz)
- 8x Pylontech US3000C (~28kWh)
- 1.7 kWp solar via MPPT (DC-sided)
- (Planned for later: ~8-14kWp AC-Out1 sided solar via Fronius inverters, 3-phase)
I've read a lot through guides and this forum, but am still not sure about unbalanced loads at the generator. Our power metering shows a base load of about 0.3-0.5kW per phase, highest imbalance we've seen so far was a difference of about 3kW between phases. Therefore my following question:
To which limit will Quattros compensate a single-phase unbalanced load? Up to their 70A max. battery charge current in worst case of an empty battery? Would that mean 2*70A, so about 6.5kW, could be transferred via DC-side to one phase of load balancing? Only for a short amount of time, of course, as the Quattros are only rated for 4kW continuous power.
Additionally, can Quattros be programmed to disconnect the generator on a certain level of unbalanced load or is this up to the generator?
Thanks a lot!