question

alan-whyman avatar image
alan-whyman asked

230 between live and earth

Hi on a 48/375 inverter I am getting 115volts between live and earth and 115volts between neutral and earth. But i need all of the 230 volts between live and neutral and 230 between live and earth meaning the neutral should be ground also. I noticed in the manual on page 12 this is possible with the larger inverters by moving a wire to a different connector but does not seem possible with this smaller one. Thanks if anyone can help i can solder to move the wire if any one knows where to put it.

Phoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Page 12 of the manual shows what to do at the small inverters (250, 375 and 500VA).

1652877743059.png


1652877743059.png (551.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.