Does good PV current at controller eliminate PV wiring as the problem?

I'm not dealing with an ongoing problem but trying to learn from people with more experience so that I can be more efficient in the future.

If you disconnect the PV wires from the controller and measure amperage across the wires and get an appropriate reading for the PV array - does that completely eliminate the PV wiring and array from being a possible cause of whatever issue? I know that voltage can go through wiring that is not really capable of carrying substantial current - but unless there is something I don't know substantial current really can not - in my experience, it will arc and/or burn the bad/inadequate wire or connection and usually just make it completely inopperable.

Is there something about this I just don't know? If not, it seems like this one measurement would eliminate a lot of possible causes of a charging issue.

solar
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@David LaFerney

PV under load is important.

A pretty dangerous method you propose of checking using a meter to check short circuit amps.

In comissioning a system, you check polarity, VOC. To verify your string is correct.

Connect fusing/ Switch on dc disconnects.

Then check voltage drop under load, cables and cable connections, terminals for warming (usually indicates high resistance). If there are no issues, you should be golden.

Also the cable connections should be checked regularly. Especially if the initial check/comissioning was in cloudy or less optimal conditions.