Quattro 12v 5000va wire socket connection problem AWG 4/0 - 120mm2

The manual prescripts that we need to use 120mm2 wire, but the sockets don't fit on the quattro.

Problem solved by cutting the socket, but offcourse this is not the correct way of working.

What am I missing here, why are the connection points to small for the correct wire sockets?

I have 28 mm wide 120mm2 sockets.

img-20220429-193653.jpgimg-20220429-210242.jpg


connection issue
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

The manual I looked at mentioned 90mm sq cable.

quatro-5k.png


0 Likes 0 ·
quatro-5k.png (109.5 KiB)
Frank avatar image Frank commented ·
Very strange, below the manual i have
0 Likes 0 ·
1 Answer
Frank avatar image
Frank answered ·

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
You have the correct manual.


Split the difference? 1 90mm cable plus 1 120mm cable?