Pylontech US3000C BMScan to EasySolar I

Have set up comms between US3000Cs and EasySolar II with no issues. Trying to get working on an EasySolar I, which only has a VE.can input, no BMScan. Have wired up my own Type A BMScan cable from batteries to inverter, checked and is all okay.


From what I could gather it is still possible to use the VEcan port as a BMS can, but I’m having no luck getting the batteries to show up on the CCGX device list.


Hopefully someone can shine some light on this for me.

BMSPylontechEasySolar All-in-OneVE.Can
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

This maybe of help https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

The battery with the empty link port 0 is the master battery. You must use the VE.Can to CAN-bus BMS type B Cable, part number ASS030720018 for connection with US2000/US3000/UP2500; and VE.Can to CAN-bus BMS type A Cable, part number ASS030710018 for connection with US2000C/US3000C/UP5000/Force-L, you cannot use the cable supplied by Pylontech.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

You need to set the can port from VE.Can (250kbis/s) to BMS-Can (500kbit/s). That is also explained in the document linked from Paul.