Victron BlueSolar 150/45 with 3x160w panels in series connected to 840Ah lithium iron battery.
Controller shifting from bulk to absorb to float very early, leaving the batteries undercharged.
The Victron MPPT control, hard wired to the Blue Solar shows a voltage about 1v higher than that of the battery. The battery voltage is monitored at a Magnum Energy Battery Monitor shunt and by direct read from each of the three Overkill Solar BMS.
I have seen posts to the effect that resistance in the circuit can cause the BlueSolar to "see" too high a voltage, so all connections have been cleaned and checked.
Finally, I measured the voltage at the battery side terminals of the BlueSolar with an external meter. The voltage at the terminals matches exactly the voltage reported by the Magnum and the BMSs and this voltage is 1v below the volage shown on the Victron MPPT control.
So, right now I have:
-- MPPT control reporting 14.4v., Absorb stage, about 24.x amps.
-- BMS reports 13.31v. Logs highest voltage ever as 13.67v.
-- Magnum reports 13.4v
Sounds like a defective controller to me, but all input welcomed.