Hi, I have just recently joined the community of sun loving energy seekers by getting a Victron EasySolar 48/5000 system with solar panels and pylontech batteries installed by a reputable installer.
The system is working extremely well but being based in South Africa we currently get a lot of power cuts and one thing I am noticing is that Earth Leakage circuit breaker is tripping whenever our main power is restored from the grid after a power cut. We have never had issues with Earth leakage problems before and I tested the system by manually switching power off to the inverter from the mains and then switching it back on (It trips the breaker) I did this a couple of times and it tripped nearly every single time.
I then bypassed the inverter setup via the changeover switch and simulated a "power failure" from the mains and switched it back on again and the Earth leakage did not trip. I did this about 4 times and not once did the earth leakage trip, so basically it means that for some reason the Victron is tripping the breaker
I have contacted my installer and electrician but I am still waiting for a response from them with regards to this. so I thought I would ask you friendly folks on this forum if anybody may know why the system is doing this?