Parallel MP2 3K with MP 2K to add capacity

If I install an MP2 3K (12/3000/120-50) now and later decide I want more output capacity (wife wants to run AC, Microwave, Induction Stove all at same time), can I add a MP 2K in parallel to MP2 3K with synced output to single 120V line? Or is parallel only available for equivalent sized units?

Thx.

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Kevin Windrem avatar image
Kevin Windrem answered ·

Parallel units must be the same model, running the same firmware. It is also recommended they be purchased at the same time to avoid differences in manufacture (parts differences) that could affect proper load sharing.

More info here:

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

You would also need to increase your battery bank in order to supply the increased load.