Why AC-coupled Fronius is FQ shifted OFF when only one phase is missing?

Strange situation.

Today one phase (L3) in my 3-phase grid vanished.

System switched to inverting but AC-coupled Fronius immediately reported state 105 and switched off.

I did not expect this since battery was at 57% SOC, loads where around 900W and expected Fronius's production should be around 600W (it was 10AM and cloudy). There was no need for FQ shifting. I calculated the expected Fronius's production from MPPT production that was going on without problem. MPPT was producing 360W and there is 10/6 power ratio between Fronius and MPPT.

At that point I switched grid off with the main switch. Now all three phases are gone.

Fronius restarted and begin producing as much as expected.

Around 3PM I flipped the main switch back on to see if the missing phase is back.

Immediately Fronous stopped with the "ERROR" on the display and refused to turn on production with the state 105 reported. (Phase L3 was still missing)

Turning the main switch off again "fixed" Fronius's problem and it started producing.

My questions are.

When system switches to inverting because 1 phase is missing how this can influence the AC-coupled Fronius?

What is different between 1 phase missing and all 3 phases missing?

Obviously something is different, but what and why?


phase.jpg

Can someone explain to me, why is my AC-coupled Fronius frequency shifted now to the point that is completely OFF?

There is enough load from the house and half of the 20kWh battery waiting for the energy. MPPT chargers are working and Fronius should produce almost 800W with the sun available.

I think there is a bug in the MP-II firmware or ESS assitant that prevents AC-coupled inverters from producing when only one phase is missing.

screen-shot-2022-04-09-at-83406-am.png

And here the proof.

After disconnecting my system from grid completely, Fronius started producing.

screen-shot-2022-04-09-at-84702-am.png

AC PV Coupling
phase.jpg (154.6 KiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·

@MarekP

Just a thought, but frequency shifting control will be a little messed up as working on grid and offgrid is different, and you now have a mix.

Maybe you would need to have switched as a group on? Then all switch to inverting when one phase is off. Unless you have a reason why they are not switching as a group?

I could not say for sure as I have never experienced this scenario.

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Vangelis Beligiannis avatar image
Vangelis Beligiannis answered ·

Hello. I have exactly the same problem with 3 multiplus Ii48/8000 and a fronius symo. In my case it is even more strange as the output frequency is 50Hz and I still get the 105 error for overfrequency. When i switch off all phases the error goes away! I contacted fronius and they said it has to do with the Victron output. If you contacted victron and they did not answer, it means they have no idea. I will get back if I find something.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Vangelis Beligiannis avatar image
Vangelis Beligiannis answered ·

So back to the problem with more details.

The Fronius inverter will show the error 105 when phase L2 or L3 are lost.

If L1 is lost than the inverter operates normally.


I contacted my dealer as well.