Hi
I recently set up a small UPS using a MultiPlus 12/800 and a 105AhC20 AGM battery. Everything works as expected and I'm also running Venus OS on a Rpi 3B to be able to monitor the system.
The MultiPlus is working as standby UPS (no ignore AC settings), so it only uses the battery/inverter if AC goes down or misbehaves.
Battery Monitor on Venus is set to MultiPlus on VE Bus.
I noticed that SOC keeps dropping about 0.5% every day. This should not happen as the battery voltage is 13.4V (temp. comp.) and no load is applied. I also see a strange random load of 1A being drawn from battery. This is probably related.
I was able to catch one, see below...
I been thinking...
Is this maybe caused by temperature compensation? (temp raising so charger lowers the voltage maybe causing false current readings?) If so, this can also confuse SOC calculation?
Any thoughts and help would be very much appreciated.
UPDATE:
So, if we had solar/external chargers or loads connected we shouldn't use the MultiPlus to calculate SOC, but if we have a basic setup like mine, with no external charger/loads, I think that would be a good idea that internal calculation could hold SOC at 100% after entering storage mode and if inverter was not being used, so it would ignore 'noise' readings like the ones I get that I think are caused by temperature compensation adjusting voltage.