Parallel Inverters

A new Victron multi 24/3000/70 and a 18 month old phoenix 24/3000, can I connect them in parallel?

multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

No.

This is clearly documented.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

@Comboyne Farmer

As @nickdb says and to make it even more clear, I highly recommend to read the documentation for Parallel, split- and three phase VE.Bus systems