question

abode-repair avatar image
abode-repair asked

Li-ion Charge Settings

The battery manufacturer wants the storage voltage on the charger set to 13.6 volts. Under the Li-ion settings on the app for the blue smart charger does not allow the setting to be changed from 13.5V. Is it better to use user defined schedule and edit the storage voltage to 13.6 or use the LI-ion settings with the lower storage voltage?

bluesmart ip22
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

Hi @abode_repair again,

for that to happen you need to enable Advanced settings in the VictronConnect app and then go to advanced battery settings, type on the battery preset and and click on user defined. This will allow you to change settings for storage mode voltage.

It is completely up to you. 13.50V in the lithium setting is absolutely ok for storage.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.