Some comments about an EasySolar-II

I broke the bank and I bought an EasySolar-II GX, 48V / 5kVA with a 250 V / 100A SmartSolar charge controller.

To my dissapointment, the SmartSolar charge controller would not start. Eventually, I fixed it, but I had to take the cover off and poke it with a screwdriver.
Can anyone guess, from the attached image, why it would not start? :D

My second concern is the H01N2-D, 25 sq.mm cable used for connection to the PV input.
This is typical electric arc welding cable with a voltage rating of 100V AC / 150 V DC, but it is used on a charger that can accept up to 250V input.


20220315-094952.jpg

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The small red wire at the 2-pin plug have to be at the H (left) contact not the L (right) contact.

There was a batch of 400ish units manufactured with that miswiring.

https://community.victronenergy.com/questions/119025/easysolar-ii-gx-5000-250100-mppt-off.html

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

christine34 avatar image christine34 commented ·

I didn't notice that until reading your comment. tunnel rush fnf It is due to a manufacturing defect.



0 Likes 0 ·
mondeoman avatar image
mondeoman answered ·

Another thing I noticed: this 4kW / 5 kVA inverter draws only 20W at no-load. That is quite impressive.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

And there was no more money for a reasonable Victron VE.Direct cable because the bank went bankrupt.