Dear all,
I have:
- Multiplus-II 48/8000 v494
- LiFEPO4, Orion BMS via Can, 48V
- PV Inverter parallel to ac-input
- Energy meter EM24 on PV inverter, configured as PV-Inverter
- Cerbo GX v2.84
- ESS & DVCC enabled
- Scheduling charge disabled
Setting up in ESS the mode with or without BatteryLife the charge power is going from 0- 100W, not more, even there is excess PV power:
Setting the ESS mode to Keep Battery charges, the charger charges well with the maximum current.
Why are there no dots from the PV Inverter to the Multiplus ? It seems that for some reason / missconfiguraion the excess power is not calculated well.
It seems that the Consumption is almost as high as the PV production.
Do you have any suggestions ?
Many thanks
Andreas
Some config Screenshots: