question

jaeger avatar image
jaeger asked

SmartSolar 75/15 Absorption Voltage Higher than Set

Finally have a clear cold day and am able to test my SmartSolar 75/15 installation. I have a pair of new 100ah 12v AGM deep cycle batteries that were only slightly discharged and a 100 watt 20v solar panel supplying the charge.

To the point, the configuration screen of the charge controller shows the absorption voltage set to 14.4 volts, but the app shows the actual voltage being produced is a consistent 14.67-14.68 volts. My BMV-712 Battery Monitor confirms the voltage as 14.65 volts which is close enough. Reading voltage at the batteries with my older voltmeter shows 14.58 volts.

My concern is the battery manufacturer says 14.7 volts is the high end of the absorption range and I don't want the controller to ever exceed that. Since the controller is already exceeding its own configured voltage, I'd really like to know if there's a risk of the voltage going even higher.

Thanks.

@Jaeger

img-4367.png(208.5 kB)


img-4366.png(193.8 kB)


img-4365.png(192.7 kB)

MPPT Controllerssmart solar set-up help
img-4367.png (203.6 KiB)
img-4365.png (188.2 KiB)
img-4366.png (189.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
boekel avatar image
boekel answered ·

This question comes by every day, it is probably due to the temperature compensation. Colder = higher voltage.

Your battery manufacturer also states a temperature (usually 20-25 degrees C) where the maximum voltage is stated.

Maybe the Manual can be made more clear on this? (@Guy Stewart (Victron Energy Staff) ?)

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·

Yes; and the app. We’ll work on that; thanks!

0 Likes 0 ·
jaeger avatar image jaeger commented ·

The math works out almost exactly. The temperature during the test was about 2 degrees C and based on a standard 25 degree setting, 23 times the voltage adjustment resulted in almost the exact voltage shown. Thanks!

0 Likes 0 ·
mark2 avatar image
mark2 answered ·

I wanted to bump this as I have a similar issue after having LiFePo4 batteries installed yesterday. Absorption voltage is set to 57.6 as per manufacture recommendation, however the BMV and CGGX both display voltage of 57.9 at the end of bulk. The charger is set to 'Lithium' battery type which should disable temperature compensation. In any case, the temperature yesterday was around 20 degrees C.

I am concerned that I could be overcharging them - should I reduce the absorption setting by 0.3V?