Grid setpoint

Hi all

So my playing around with setting the grid setpoint to force charging has led to another question:

What if the grid setpoint is set to (for example) 5000W, my AC loads are 1000W and the maximum current into the batteries (48V) is 60A?

By my maths, I'm using 4000W - will the inverter drop the grid draw to around 4000W? If not, where does the extra energy go? (Multiplus inverter, CCGX in ESS mode)

Similarly, if the batteries are full, will it also drop the grid draw?


Thanks :)

MultiPlus Quattro Inverter ChargerESSCCGX Color Control
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
boekel avatar image
boekel answered ·

Yes, the grid setpoint has to obey the rules:

-Battery settings

-Input current limit (works both ways)

-maybe some other things :)