MultiPlus 3000VA 24V Remote On/Off issue

Hi all,


I have problem trying to install simple 3-way switch as a remote On/off/Charger only switch for MultiPlus.


Inverter is turned ON from the original switch.


Shorting H terminals Left-Mid turns Inverter ON

Shorting H terminals Right-Mid seems to be turning it OFF (Maybe goes Charger only mode?)

The problem is: While keeping all terminals open with switching the remote switch in the middle, the inverter is still turned ON.


I am not using any remote panels with the system. I have VE.BMS but the Remote Control port is empty.


What I am doing wrong?


Thank you!

remote console
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

on the main board there is a remote control blue plug it has three connections its looped from factory on the left to mid as closed - opening this loop Mid to left turns the inverter charger off - looping the mid to right of the plug turns the charger only on