Claudio Paredes Budon avatar image
Claudio Paredes Budon asked

Multiplus II GX with generator, output 2 disconnect when I connect loads.

Hi everyone,

I have a Multiplus II GX with pylontech batteries, when I connect the generator there have good voltage and frequency, it charge the batteries and it's voltage in AC_out_2. The problem is when I connect something to that line, the multiplus disconnect the generator in AC_in and it's don't show any error.

Multiplus-IIGeneratorac out 2
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@Claudio Paredes Budon

We had a load on ac out2 that used to do that to the generator. It was a pump control with a neutral earth leak causing the "grid rejection".

Check the wiring.

0 Likes 0 ·
1 Answer
Paul B avatar image
Paul B answered ·

could also be that the load is two great for the generator and the low voltage cut off is disconnecting the generator reduce the current input limit