Victron 3 phase ESS - AC power on 1 phase swinging wildly

Hi Victron Community, I'm new here - hello!

I just installed a three phase Victron system with 3x 5kVA Multiplus 2's, 1x 450/200 Victron MPPT (13kW Solar), Cerbo GX, 2x ET340 (Grid + Solar PV). I also have 3x 5kW Solaredge inverters on the AC side. I have a 160kW battery bank with Batrium BMS.

img-0301.jpg

I've had it up and running for about a week and it's has been working beautifully - ESS was working well and have drawn nothing form the grid. Yesterday something weird happened and the feed in and draw from the grid was swinging wildly between -4kW and +4kW. It seemed to be happening on Phase 2 only and it seemed like it would start off with the correct readings for the grid meter and AC loads and then it would ramp up and suddenly think 8kW was being drawn from the grid so would ramp up to compensate then suddenly the grid meter would read 0 and it would ramp down again only to repeat again 30 seconds later. screen-shot-2022-02-21-at-11312-pm.pngscreen-shot-2022-02-21-at-10218-pm.png

I think it started when I connected a big load to the AC Load side initially (3 phase car charger 17kW total) but continued after I switched it off. I turned off all the loads on that phase and it still continued. Kinda feels like it went into cardiac arrest! Also - the recorded AC input current on that phase dropped to 0 at the time - it definitely wasn't 0, I confirmed this with a fluke current meter.

screen-shot-2022-02-21-at-12446-pm.pngscreen-shot-2022-02-21-at-13545-pm.png

My initial thoughts were that it must be the grid meter feeding incorrect data to the Cerbo and this morning was going to swap the ET340's to see if it fixed it, but fired it all up first and it's been working perfectly again for the last 6 hours. It's not possible that the 63A limit of the ET340 was exceeded - I have a 50 amp breaker on it and I just don't have any loads that are big enough. Any ideas?

ESS3 phase
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
nickriley77 avatar image
nickriley77 answered ·

An update: Not sure what happened for that few hours but the system has been working flawlessly since then. I'm assuming it was a glitch with the ET340 - some sort of creeping with the current sensors or something on phase 2. No need to answer I'll post something if it happens again and I find a solution.

My highest compliments to the team at Victron - this gear is absolutely amazing. Everything is top notch from the physical equipment to the IT side (VRM etc). I'm so impressed - this system is better than I ever could have imagined.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @NickRiley77

I don't know if you use external current sensors, but it seems the socket for them on L2 was malfuntioning. to fix it usually is enough to insers a 3,5mm plug a couple of times and remove again.


0 Likes 0 ·
nickriley77 avatar image
nickriley77 answered ·

Hi Daniel thank you - I only use the ET340’s - one for grid and one for pv. No other sensors

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickriley77 avatar image
nickriley77 answered ·

Quick update in case it helps anyone else - I clearly hadn’t understood what Daniel was suggesting - I had the same issue again and put a headphone jack in to the external current sensor socket on the multiplus 2 a couple of times and it looks like it has sorted it completely. So it wasn’t a fault with the ET340 like I had thought.