How do I configure my 250/60 to keep the voltage high and stop stalling my turbine?

When I turn on the water supply to my pelton wheel (smart drive motor, configured to run at 205 V AC with no load) my MPPT load slows the revs way down, and lowers the voltage to 70 V. This then makes my 110m cable run with higher amps, and less efficiently. Instead of the expected 900 to 1000 Watts, I'm only getting 350 W.

Is there a way to choose a minimum voltage on the MPPT, say 150 V and lower current, letting the turbine spin at the best revs?

MPPT ControllersHydro and Wind Power
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
JohnC avatar image
JohnC answered ·

Hi @stokie77

Presuming rectified ac and independent from any solar panels. And the dynamics of mpp tracking a pelton wheel way too slow for something designed for pv.

There's no way to limit input V, but the mppt can be limited in output Amps. Try that.

And if you've Youtubed your setup, would love a link.. :)

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stokie77 avatar image stokie77 commented ·
Thanks John, Yes, I added the 250/60 unit purely to control the hydro power. Rectified AC coming in from the smart drive generator.

I discovered the maximum amps setting with the bluetooth VE Connect app on my phone not long before you answered, previously assuming that I was looking at a system-wide amps setting for my Easy Solar unit.

I adjusted the amps limit from the default 40 A down to 7 A, hoping that this will be about right when my replacement pipe fittings arrive - 96 PSI water pressure was a bit much for the glued joints in my updated turbine setup. Looking forward to having a stop valve closer than half a km too.

I guess I'll do a basic YT video of my system once it's all operational, and I'd be glad to send you a link.


0 Likes 0 ·
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

???

Is that motor connected to the PV side of the MPPT together with the PV panels?

If yes, there is nothing that you can change at the MPPT. It is the PV array that can't deliver higher voltage with that load connected.

The voltage/power at the PV side is coming from the PV array, not from the MPPT.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stokie77 avatar image stokie77 commented ·
Hi Matthias, no, the 250/60 unit is just for the hydro side of things.
0 Likes 0 ·
stokie77 avatar image
stokie77 answered ·

Hi Matthias,

My PV panels are connected to my Easy Solar system.

My hydro generator is connected to my Victron 250/60 charge controller.

Both charge controller outputs are connected to the same battery connectors.

My MPPT sees the power coming from the generator as soon as it starts to spin, and it either loads it up with too many amps to let it spin up to an efficient speed, or drops the amps so low that it spins past the 261V cutout level.

Why can't it remember that its limit is 250V, and adjust the amps load accordingly?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image snoobler commented ·
It's not about remembering. It's about he circuitry being designed to handle up to 250V. It can't regulate it in any way. If you put a 251V+ source on it, you may blow it up.


Again, you're going to have trouble in absorption mode. When the MPPT starts reducing current to hold absorption voltage, it's going to unload the turbine, and it will spin faster.



0 Likes 0 ·