Quattro 24v 5000 major capacitor bank explosion

I have a Victron Quattro 5000 that runs off of 24 volts in TV live truck. In our current unit the capacitor bank between the heat sinks have completely blown up. We have purchased a new one, but before installation, looking for info on what circuit those capacitors are associated with so we don't blow up the new one.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@AZ Ryno

Usually that is caused by high DC ripple. Upgrade your battery cables. 95mm² x2. Check you do not have too many connections between the inverter and battery. And make sure the battery you have connected sized for the job.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Johannes Boonstra (Victron Energy Staff) avatar image
Johannes Boonstra (Victron Energy Staff) answered ·

Also make sure the balance between battery capacity and inverter is correct. the inverter needs >250A so you need 500Ah lithium or 1000Ah lead acid