Can the Multiplus II do this?

Hello, I'm looking into purchasing a Multiplus II 48v 5000 watt and would like to know if it can be configured to do the following:

*Charge (Pylontech 4x3.5kwh) batteries at night on cheap (Octopus Go UK) night time tariff.

*Discharge during day when electricity is expensive.

*Pull from grid if A/C loads exceed the inverter's 5000 watt capacity.

We have a grid tied Easysolar GX II in our office that functions in a similar way, but it has solar PV attached. However, when there is no sun it functions in the way described above. Excessive loads above battery capacity are topped up from grid power.

That unit is also able to function as a UPS when we have a powercut.

Any information would be very much appreciated!

Phil


Multiplus-IIgrid
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

craig-revell avatar image craig-revell commented ·
Hi Phil,


I am thinking of using the Multiplus with Pylon US5000s, interested in your schematic and what you used to interface with Octopus to make best use of their tariffs.

KR

Craig

0 Likes 0 ·
7 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Yes it can, using the scheduled charge feature as part of an ESS system with a GX device (or using the MultiPlus-II GX model).

https://www.victronenergy.com/media/pg/Energy_Storage_System/en/configuration.html#UUID-eea56ee5-efe2-0fce-ab6f-ba51656dfb45

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

philthevictronboy avatar image philthevictronboy commented ·

Hi Guy, thank you for your answer, just to be 100% explicitly clear: solar is not required for the Multiplus-II GX to function in this way? From my reading of your link, that seems to be the case, but I want to make 100% sure.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ philthevictronboy commented ·

I confirm that Solar is not required, it is sufficient to program the system to charge the battery from the AC input.

A GX device, and a MultiPlus ARE required. Though these can be in the same device such as the MultiPlus-II GX.

0 Likes 0 ·
philthevictronboy avatar image philthevictronboy Guy Stewart (Victron Community Manager) ♦♦ commented ·

Fantastic, that's the exact item I'm looking at "VICTRON MULTIPLUS-II GX 48/5000/70-50 230V". Thank you very much Guy.

0 Likes 0 ·
seb71 avatar image
seb71 answered ·

Keep in mind that there are some loses of energy when you do this (charging/discharging the battery and converting from AC to DC and back to AC).

The day/night price difference from your electric power company must be high enough, otherwise you end up losing money.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

philthevictronboy avatar image
philthevictronboy answered ·

Thank you both for those answers. Could I ask, do you have any idea of what the round trip losses would be? I knew there'd be some, though I was only factoring in around 10% in my calculation.

The ratio on night/day is 7.5p to 31.1p per kWh, so it's over 4x cheaper at night.


Thanks again.

Apologies, I think I found the answer here for this question:

https://community.victronenergy.com/questions/56351/multiplus-485000-efficiency-curve.html


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

Besides the inverter losses, there are some battery losses, too.

But I didn't expect such a huge price difference between day and night tariffs.

You should be set.

0 Likes 0 ·
philthevictronboy avatar image philthevictronboy seb71 commented ·
Great! Thank you.
0 Likes 0 ·
wkirby avatar image
wkirby answered ·

I also have Octopus Go (5p / 16p) and this setup works well for me.
I have a 3kVA MultiPlus, so I only charge at 1.7kW during the four hour period at night which is not enough to completely fill the battery (also 4x 3.5kWh Pylontech) from empty.
You have got 3.5kW charging capacity, so this is plenty to fill up during the cheap hours. Just make sure you have leave space for solar power to fill the battery during the day. Perhaps limit the night time charge level in the charging schedule. Summer is coming,so I am starting to reduce my night time charge level to allow space for solar power.

When it is stormy (like it is now), then I set the system to keep batteries charged and if there is a network outage my battery is full.

For me, the round trip losses are small next to the price differences of the tariff.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

philthevictronboy avatar image
philthevictronboy answered ·

@wkirby, thank you for your answer. What you're talking about is the type of set up we have in our office. Grid charging at night and then in summer I play a bit of a guessing game and reduce how much charge at night to let the solar fill the batteries and run the office in the day. (Though the intention of this system was more as a UPS as we kept having power outages.)

What I am looking at now is having only batteries and no solar for the moment, as I'm not sure how long we'll be staying in our current home. It's a lot easier to take the batteries and inverter if we were to move than getting solar off the roof!

It's a sort of mitigation strategy against the huge price rise we're about to face. (With the added bonus that we'd be using, on average, greener night time energy and reducing dirty fossil fuel energy use in the day.)

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pau1phi11ips avatar image pau1phi11ips commented ·

I'm starting to look into Home Assistant. It looks like it would be possible to get that to set the charge level (via MQQT) for the Multiplus each day based on the predicted weather for the following day. That's a very distant future project though.

I intend to get some solar panels in the garden that will feed back into the mains. Since the ET112 is just after the main meter the Multiplus in the van will actually charge the battery during the day if there's excess power so as little as possible if feed back to the grid.

0 Likes 0 ·
pau1phi11ips avatar image
pau1phi11ips answered ·

I have a Multiplus II in my campervan with a 7kWh self built LiFePO4 battery.

I'm currently doing exactly what you want to do with it. I charges at night on the 5p Octopus Go rate and discharges into the house during the day. My average cost per kWh for the whole day is ~7p.

I set the target pull from the grid to be 20W and the Multiplus tracks the load from the house via a ET112 meter with Zigbee connection. You can set the max the Multiplus will output too. Mine's at 1000W. The battery isn't big enough for the total house usage in a day so it's just taking the baseload and smaller usage during the day but it won't be powering 100% of the kettle for example. No need to stress the components in the Multiplus if I'm not going to benefit from it.

One plus point is the 600W of solar on my van also charges the same battery and hence my house! :)

1645093148677.png


1645093148677.png (63.0 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

philthevictronboy avatar image philthevictronboy commented ·

Interesting, that sounds very similar to our office setup, though your topology is slightly different:

1645094010438.png


0 Likes 0 ·
1645094010438.png (51.1 KiB)
Ben Watts avatar image
Ben Watts answered ·

This is a super helpful thread, I'm thinking of getting a Victron with similar objectives in the Octopus tariff, being in the UK I realise our "solar season" isn't the longest.

While it's pretty clear you can make the payoffs work if you can buy power at 7.5p/kwh, this really is a loss leader for Octopus. Even if you look at only the wholesale prices (https://www.nordpoolgroup.com/en/Market-data1/GB/Auction-prices/UK/Hourly/?view=chart), it's very rare that power is below £75/mwh, even putting aside any grid and other charges.

The agile tariff sometimes has big price plunges, but I'd be surprised if they're often enough, or if anyone yet has developed the software that's smart enough to properly take advantage of them.

I guess this points toward opting for a smaller battery and (if possible) charging direct from solar DC to minimise efficiency losses.

Out of interest, does anyone know if battery life runs contrary to the above? I kind of suspect that batteries would much prefer a deep charge every night to sporadic daytime charging.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
Lithium batteries don't care, an ESS by default is in a constant state of charge/discharge.
0 Likes 0 ·
ejrossouw avatar image ejrossouw commented ·

The bank however has to be charged above 90% maybe once a month (requirements can vary by product) to allow the cell balancing to take place if it has not reached that level in e.g. the past 30 days.

0 Likes 0 ·

Related Resources