HI
I have an an alarm coming up on the cerbo stating,
Lynx smart bms 500
alarm
#222
I cant find anywhere that tells me what this is?
System has,
lyxy distributors and smart bms
victron lithium batteries
Cerbo GX
Multiplus 5kva
Thanks
Grant
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
HI
I have an an alarm coming up on the cerbo stating,
Lynx smart bms 500
alarm
#222
I cant find anywhere that tells me what this is?
System has,
lyxy distributors and smart bms
victron lithium batteries
Cerbo GX
Multiplus 5kva
Thanks
Grant
Hi @IandDIndustries,
Alarm #222 means that the connection with Lynx Distributor B is lost. Did you by any chance change the address (with the dip switches) of that distributor? That would cause such error.
The only way to get rid of the alarm is to remote off and remote on via the connection terminal (see Lynx Smart BMS manual Section 3.3).
FWIW, the error codes are in the manual for the Lynx Distributor (https://www.victronenergy.com/media/pg/Lynx_Distributor/en/operation-lynx-distributor.html#UUID-d7d39f2a-36ed-0965-7936-34a632c0dd24) and should appear in a readable format in VictronConnect.