#25 Pre-Charge error on Lynx/Quattro system

Hello,

We have a system consisting of a Victron Lynx ION/BMS/1000A and a Victron Quattro 24v/8000va/200a charger/inverter.

The system completely hanged up after showing the error “#25 Pre-Charge Error”. The batteries weren't being used when the error showed up (the system was in "pass-through" mode).

Has anyone encoutered the same error ?

Thanks in advance.

battery chargingerrorlynx shunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

On looking up the error maybe its because

The Lynx Ion + Shunt will not start if there is more than 10A drawn by the system during pre-charging


Power up procedure

1.Make sure that all energy consumers are switched off before starting up the system.

2.The Lynx Ion + Shunt will pre-charge the system before closing the safety contactor.

3.Press the START-button on the front of the Lynx Ion + Shunt to start the system.

4.Now the system is being pre-charged. The safety contactor is closed as soon as the voltage rises above 80% of the battery voltage.

5.If the status LED is continuously on, then the system is running and ready for use.


The Lynx Ion + Shunt will not start if there is more than 10A drawn by the system during pre-charging

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

excalibur83 avatar image
excalibur83 answered ·

alarm-pre-charge.pngHello,

I've met the same alarm (trhu VRM Portal sending a email) which is "pre-charge error". A second email was sent within a minute cancelling the alarm. Looking at the portal, we can see battery start discharging about 10pm till alarm released (1:18AM) then battery starting to charge "normally". Installation includes a Lynx (connected to DC board systems) + Multiplus which was normally connected to grid (boat on shore). It appears shore grid was off from 3PM to 1:17AM which explains battery drawn but why alarm was triggered because system didn't shut down at all ?


alarm-pre-charge.png (479.8 KiB)