question

enerhuman avatar image
enerhuman asked

Can not recieved Power Input on Quattro

I have 3 Quattro equipment, 48 amp working as triphasic.

The equipment of a wind generator does not want me to receive load.

These are the values that I put in the Grid

1644000057518.png


1644000106661.png

1644000127383.png


MultiPlus Quattro Inverter Chargerwind
1644000057518.png (31.1 KiB)
1644000106661.png (51.2 KiB)
1644000127383.png (38.4 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@Enerhuman

Which input are you using? Ac1 or ac2

Maybe it is a loss of mains thing?

I have not used a wind generator on a Victron, but with a petrol or diesel is cannoften be the LOM detection.

1 Like 1 ·
enerhuman avatar image enerhuman Alexandra ♦ commented ·
AC 1
0 Likes 0 ·
1 Answer
Paul B avatar image
Paul B answered ·

The incoming power is 130v your voltage disconnect is 140v.is the input going over 140v.also as the re connect is 125 it will stay off


Could also be the Hz if it goes over 65 it will also disconnect

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.