My ESS system is not using battery power when grid fails.

ESS system parralel on the electric instalation (using only ac-in) when switch off the grid the 3fase system is not feeding battery power back to the electric instalation through the ac-in.

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wkirby avatar image
wkirby answered ·

That is the correct operation. A system should never feed back to grid when grid fails (or it is switched off).
If you want to feed loads when grid fails then you need to connect the loads to AC-OUT.