MPPT RS double string voltage

Hello,

i've an existing pv system.

150 modules with 8 strings.

one string have a voltage on cold weather max. 870V

at the moment connected to normal pv inverters (SMA tripower)

behind that i have powersupplies they made 48V for telco systems with batteriecontrollers and so on.

PV => Inverters to 240/400V => Powersupplies to 48V with batteries

now i have the idea to change that und have directly

PV => MPPT => 48V with batteries

I have now a small system running with a few MPPT RS and it works fine. But the MPPT RS have a limit with 450V on the PV site. When i will use the MPPT RS i must be change the cabeling on the PV site. That will be a lot of work of the house top and empty tubes have not enougth space for the double of the cables.

My Questions:

1. Can a use 2 Trackers of MPPT RS in serial to extend the string voltage to 900 V ? I think that would be difficult ...

2. Is there a plan of an MPPT with a higher string voltage on the victron site ?

Thanks

Thomas

MPPT Controllersmppt rs
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi, sorry: no and no.