Multiplus II and Victron MPPT with Lead Carbon Battery Issue

Good Morning Community,

We have a customer with an existing Victron Multiplus and MPPT installation (done by solar installer) who is not getting charging current into the batteries in mid afternoon after the Lead Carbon batteries hit around 80-90%. This is a completely Off-Grid installation with back-up generator. 14kW of Solar available. 40kWh of Lead Carbon batteries. Here is the graph.

Diagnostic Suggestions welcome...

Multiplus-IIESS
img-2842.jpg (263.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
boekel avatar image
boekel answered ·

Judging by the graphs, the batteries doesn't seem to accept more current.
It would help if you post the battery voltage / current graph, and not (only) the solar graph.

It looks like there was a peak in power usage around 9:30 that brought the charger back in bulk, before that the current dropped fast at absorption voltage.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

safiery avatar image
safiery answered ·

Thank you Boekel . The second graph in the image has battery voltage and current from the Solar controller. Do you mean these values as measure by the 712 on the load side?