Hello,
I have a slight problem with my off grid system and sincerely hope one of you can help.
I am currently running:
4 x 230 Ah (C20) parallel in series (24V 460Ah)
1x MPPT 150/85,
2,9 Kw solar array (3 strings @ 66V)
Lynx distributor
BMV712.
Cerbo.
ECTIVE 24V/1kw invrter
Multiplus II 48V/3000W
My plan is to change from 24V to 48V, so I connected the 4 x12 batteries in series adding a Multiplus II 48V/3000W inverter/charger. (running on factory settings for now)
Now here is my problem: running the 24V system on the old 1kw inverter worked fine and the MPPT charged the battery bank correctly. (Bulk-Absorption-Float). 800 -1500W
Changing to the 48V however, my MPPT does not come out of Bulk and the solar array does not charge with more than 70-200 W, plus the battery does not accept more than 54V even though 66 are supplied.
I then changed everything back to 24V and the panels charge a good 800W and the MPPT goes into Absorption after a couple of minutes. All good again.
I retightened all the connections to torque, checked the fuses, went over the V.Connect settings of the MPPT as well as the BMV712, but no luck. Battery voltage does still not come above 54V and hence MPPT stays in Bulk.
Stumped and happy for any input at this time.
Thanks
Tom