hello, in my situation there is an overload of the grid in the region causing the grid connected inverters to fail due to overvoltage.
at the moment this happens the batteries are already fully charged, so my question is, is there a way to configure ess in such a way that the batteries are only charged at a mains voltage above 253v? so that the batteries are used as a dumpload?
setup:
1-phase
2x multiplus2 48/3000 parallel
2000Wp DC coupled(mppt)
4500Wp connected to grid(measured by em24s)
1500Wp AC coupled
ESS parallel (em24 in meter box)
lithium storage 14kwh (2-wire bms)
thanks in advance!