question

gharshaw avatar image
gharshaw asked

/Ac/Alarms/GridLost is not in the DBus on CCGX

@mvader (Victron Energy) @Scott Bender

I'm attempting to create a pushover alert with NodeRed using the Victron System node. The Dbus path: /Ac/Alarms/GridLost is missing in the node as well as on my CCGX 2.80~33 (missing in dbus-spy). I do have "monitor for grid failure" enabled on the CCGX.

Scott, I saw that you made a change in the scripts/missingpaths.json to "add support for /Ac/Alarms/GridLost". Maybe you have a suggestion as to why the Dbus path is missing?

Appreciate any help

Thank you





Node-RED
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gharshaw avatar image gharshaw commented ·
@mvader (Victron Energy)

Any thoughts on this issue ?

Thanks

0 Likes 0 ·
1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi @gharshaw , you found a bug in the nodes: this functionality was moved to a different D-Bus service a long time ago (v2.60 I think).

We'll update the node. The right path is com.victronenergy.vebus.[something] /Alarms/GridLost


Its no longer under com.victronenergy.system.


We'll fix that. Thank you for the report!