VE Bus Error 17 errors

Two multiplus units installed in parallel having contionuos vebus 17 errors units run in ess mode and have swopped madter and slave and changed comms cables any advice please

errorVE.Bus
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hi, please contact your dealer about it. They can test and otherwise replace the unit(s). There are no software settings or other fixes, other than what you already did:

- swap the network cables, including the one to the GX device

- make sure to use industrially made cables: no hand crimped RJ45 cables

- update all firmware versions.

- swap GX Device (CCGX, Venus GX. Etc).



2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dionne avatar image dionne commented ·

Thank you. Can the issue possibly be related to the ac supply to the inverter such as unsteady voltage and ac supply switching in and out due to a power outages

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ dionne commented ·

Hi, no; that does not affect this

0 Likes 0 ·